How to calculate the head pressure of the water in a loft storage tank to a shower head.


MiLKy , Sunday, 8th of August 2010 01:26:28 PM

There is a figure for the amount of metres rise (head ) to a lower outlet 
MiLKy
such as a tap or shower,but l cannot seem to find it.
 
Registered User
 
Joined: Tuesday, 20th of April 2010, 02:30:20
 
Posts: 899
 
Viewed 3668 times
 

Stevie Poo , Monday, 9th of August 2010 11:49:26 PM

2.31 ft head of water is 1 psi.  
Stevie Poo
 
Registered User
 
Joined: Wednesday, 9th of June 2010, 16:24:38
 
Posts: 1754
 
Viewed 5721 times
 

Cakey , Tuesday, 10th of August 2010 11:50:58 AM

Rule of thumb = For every 1 foot of head, the pressure at it`s  
Cakey
base will be half a pound per square inch. In other words if the waters  
Registered User
surface in the header tank is 8 feet above the tap then the static  
Joined: Sunday, 25th of April 2010, 10:11:22
pressure at the tap will be roughly 4 pounds per square inch.  
Posts: 1731
 
Viewed 12750 times
 
 
 
 

beemac , Wednesday, 11th of August 2010 08:12:15 AM

If there is a header tank the head is taken to be the  
beemac
difference in height between the water level in the header tank & the  
Registered User
point ur are looking at (here the shower/tap outlet)  
Joined: Wednesday, 12th of May 2010, 10:24:11
 
Posts: 290
If there is no header tank (direct cold water), then the head is the  
Viewed 2414 times
difference between the height to which the cold water could be pushed, &  
the height to which it is being pushed.  
 
 
p=rho*g*h  
where  
p is the pressure due to the difference in water heights in Pa (or N/m^2)  
rho is the density of the water, about 1000 kg/m^3  
g is gravitational field strength, 9.81 N/kg  
h is the head in m  
 
If you have a booster pump you will usually need some head (.5m minimum?),  
so that a flow switch can detect a flow when a tap is opened, & then turn  
the pump on (it also help prevents damage to the pump through cavitation).  
Another arrangement is to have a pressure switch in the pipes, which will  
run the booster pump, when the pressure in the pipes is lower than a set  
value (open the tap- the pressure in the pipe to the tap falls, so the  
pump turns on. Shut the tap- the pump runs until the pressure in the pipe  
to the tap exceeds a set value)  
 
Fittings, & long pipe runs reduce the dynamic head (due to  
friction/turbulence when the fluid is moving). Static head doesn't take  
this into account  
 
 
 
 
 

Satou , Thursday, 12th of August 2010 05:37:40 PM

The head is just the vertical distance from the top of the  
Satou
water level in the tank to the outlet.  